The medium transmission lines are having length lying between 50 to 150 km and they operate at voltage greater than 20 kV.
Medium Transmission line
AU : Nov.-04, April-96, 98, 99, 2000,
Dec.-09, 13, 15, 16, May-05, 09, 11,12,13,14,16,18
The short transmission lines have
smaller lengths and the power transmitted by these lines are comparatively at
lower voltages. Due to this, while analysing short transmission lines, the
effect of capacitance is neglected. With increase in length and voltage of
transmission line, the capacitive effects are dominant and they can not be
neglected.
The medium transmission lines are having
length lying between 50 to 150 km and they operate at voltage greater than 20
kV. Hence in making the analysis of medium transmission line, we have to take
into account the effect of capacitance for better accuracy.
The capacitance is uniformly distributed
along the length of transmission line. For the simplicity in the calculations,
the line capacitance is assumed to be limped at one or more points. This is
known as localising of line capacitance and it gives fairly accurate results.
The various methods that uses localising of line capacitance are
i) End condenser method ii) Nominal T
method iii) Nominal π method
In this method the line capacitance is
lumped or concentrated near the load or at the receiving end. This method
overestimates the effect of capacitance.
In case of 3 phase systems, it is always
convinient to represent a single phase instead of line to line values. Fig.
2.8.1 shows one phase of three phase transmission line.
The corresponding phasor diagram shown
in the Fig. 2.8.2.
Let VS = Sending end voltage
VR = Receiving end voltage
IR = Load current per phase
XL = Inductive reactance per
phase
C = Capacitance per phase
cos ϕR = Receiving end power
factor
As VR is the reference
vector,
The load current IR is
lagging behind VR by an angle of ϕR
It can be seen that this method is
having some limitations although this method is simple to operate. The
disadvantages are
i) This method assumes the capacitance
to be lumped near the receiving end although in actual practice it is
distributed along its length. Due to this there is considerable error of about
10 % in the calculations.
ii) The effects of line capacitance are
overestimated in this method.
This method is used for the analysis of
medium transmission line. In this method the total line capacitance is lumped
or concentrated at the mid point of the line. The resistance and reactance of
the line are divided with half the resistance and reactance on
one side and remaining half on other
side of capacitor. Half of the line carries full charging current with this
arrangement. Fig. 2.8.3 shows the arrangement used in nominal T method for one
phase. It is desirable to work in phase instead of line values.
The corresponding phasor diagram is represented
in the Fig. 2.8.4.
Here the receiving end voltage VR is
taken as reference. The drop PQ (IR . R / 2) is phase with IR. The
drop QR (IR . XL / 2) is leading IR by 90o.
The phasor sum of these drops with VR gives the voltage V1
which is the voltage across the capacitor. The capacitor current leads VC
by 90°. The phasor sum of IR and gives IS. The drop Rg f
IS •Ris in phase with Ig whereas drop ST (IS . XL / 2) is
leading Is by 90°. The phasor sum of these drops along with V1 gives
the sending end voltage VS.
Sum of these drops along with V1
gives the sending end voltage VS
Let IR
= Receiving end load current per phase
R = Resistance per phase, XL
= Inductive reactance
C = Capacitance per phase, cos ϕR
= p.f. at receiving end
VS = Sending end voltage, V1
= Voltage across capacitor
The efficiency and regulation can be calculated in the similar manner explained in earlier sections.
This is also a localised capacitance
method in which capacitance is divided into two halves with one half lumped
near sending end and other half near the receiving end. This is shown in the
Fig. 2.8.5. The capacitor near the sending end does not contribute any line
voltage drop but it should be added with line current to get total sending end
current. For convenience and simplicity in calculations only one phase out of
three phases is shown.
The corresponding phasor diagram is
shown in the Fig. 2.8.6 VR is taken as the reference phasor. The current lags behind VR by angle ϕR. The current through capacitor
C1 is leading the voltage VR by an angle of 90°. The
phasor sum of IR and IC1 gives the line current IL.
The drop ILR is in phase with I whereas drop ILXL
is leading by 90°. The phasor sum of these drops with VŔ gives the
sending end voltage Vs. The capacitor current IC2 is leading voltage
VS by 90°. The phasor sum of IS and IC2 gives
the sending end line current IS.
Let VS = Sending end voltage, VR = Receiving end voltage
IR = Load current or
receiving end current
R = Resistance per phase,
XL = Inductive reactance per
phase
C = Capacitance per phase, cos ϕR
= p.f. at receiving end
The efficiency and the regulation of the
transmission line can be obtained in the similar manner as explained in the
earlier sections.
Example 2.8.1 A 3
ϕ, 50 Hz, 100 km line has the following constants.
Resistance/phase/ km = 0.153 ohm,
inductance / phase / km = 1.21 mH, capacitance/phase I km = 0.00958 pF. If the
line supplies a load of 20 MW at 0.9 pf lagging at 110 kV at the receiving end
calculate sending end current, sending end power factor, regulation and
transmission efficiency using nominal T method.
Solution : Total
line length = 100 km
Example 2.8.2
A 50 Hz three - phase transmission line is 150 km long and delivers 50 MW at
0.8 p.f. lag and at 110 kV. The resistance and reactance of the line per
conductor per kilometre are 0.1 ohm and 0.5 ohm respectively. The line charging
admittance is 3 x 10 ~ 6 mho/km per phase. Compute by apply nominal n method, sending
end voltage and current.
Solution :
Voltage regulation is nothing but change
in voltage at receiving end from no load to full load.
Example 2.8.2 A
3-phase, 50 Hz, transmission line is 150 km long and deliver 50 MW at 0.8 p.f.
lag and at 110 kV. The resistance and reactance of the line per conductor per
kilometer are 0.1 ohm and 0.5 ohm respectively. The line charging admittance is
3 × 10-6 mho/km per phase. Compute by apply nominal π method, sending end
voltage and current.
Solution :
Example 2.8.4 A
3-phase, 50 Hz, 40 km long overhead line has the following line constants :
resistance per conductor = 2.5 ohm, inductance per conductor = 0.1 H,
capacitance per conductor = 0.25 pF. The line supplies a load of 36 MW at 0.8
power factor lagging at a voltage of 60 kV (phase) at the receiving end. Use
nominal n representation, calculate sending end voltage, sending end current,
sending end power factor, regulation and efficiency and active and reactive
voltamperes.
Solution :
Example 2.8.5
A 50 Hz, 3 phase transmission line 30 km long has a total series impedance
of (40+ j 125) ohm and shunt admittance of 10-3 mho. The load is 50
MW at 220 kV with 0.8 lagging power factor. Find the sending end voltage,
current and power factor. Use nominal method. Also find efficiency and
regulation.
AU Dec.-09, 16, Marks 16
Solution :
Example 2.8.6 Determine the efficiency and. regulation of a 3-phase, 100 km 50 Hz transmission line delivering 20 MW at a.pf. of 0.8 lagging and 66 kV to a balanced load. The conductors are of copper, each having resistance 0.1 ohm per km, inductance 1.117 mH per km and capacitance 0.9954 pF per km. Neglect leakage and use nominal π-method.
Solution :
The nominal n circuit is shown in the Fig. 2.8.12.
Review Questions
1. Derive the expressions for sending end voltage and
current of a medium transmission line nominal T-method interms of Y, Z, VR
and IR.
2. Determine the sending end voltage and sending end
current for medium transmission lines, assuming nominal n method.
3. Explain with vector diagram the nominal T method for
obtaining the performance calculations of medium transmission lines.
4. A 3 phase 50 Hz overhead transmission line has the
following constants per phase R = 28 Ω, X = 63 Ω, ɤ = 4 × 10-4 (Ʊ).
If the load at the receiving end is 75MVA at 0.8 pf. lag with 132 kV between
lines, calculate the voltage, current and pf. at the sending end. Use nominal π
method.
[Ans: 95.67 kV, 306.73 A, 0.7785 lag]
5. A three phase 50 Hz transmission line is 150 km long and
delivers 25 MW at 0.85 pf. lag and at 110 kV. The resistance and reactance of
the line per conductor per kilometre are 0.3 ohm and 0.9 ohm respectively. The
line charging admittance is 3 ×10-5 mho/km per phase. Compute by
apply nominal n method a) Voltage regulation and b) Efficiency.
[Ans.: 1.5 %, 89.92 %]
6. A 66 kW, 3 phase transmission line 160 km long has the
following constants Resistance per km = 0.156 ohm, Reactance per km = 0.5 ohm, Susceptance
per km = 8.75 × 10-6 mho
If the line supplies a load of 15 MW at 0.8 pf lagging at
66 kV at the receiving end, calculate sending end voltage, current and power
factor using a) Nominal T method b) Nominal n method.
AU : April-2000
7. Determine the sending end voltage for the following, using
Nominal method. The transmission line is 120 km long and delivers 40 MW at 132
kV and 0.8 p.f. lagging.
AU: May-05, Marks 8
[Ans.: 149.87 kV]
8. Explain the following methods for medium transmission
lines.
i) End condenser method ii) Nominal T method (middle
condenser method)
AU : May-13, Marks 16
9. A 3 phase, 50 Hz, 100 km transmission line has the
following constants
Resistance I phase / km = 0.1 Ω
Reactance / phase / km = 0.5 Ω
Susceptance / phase / km = 10-5 mho
If the line supplies a load of 20 MW at 0.9 pf. lagging at
66 kV at the receiving end calculate by using nominal π method
i) Sending end current ii) Line value of of sending end
voltage iii) Sending end power factor iv) Transmission efficiency.
[Ans.: 176.50 A, 76 kV, 0.9057 lag, 95.02%]