Electrical Machines: Unit II: D.C. Generators

Necessity of Parallel Operation of Generators

DC Generators

The generating stations either of d.c. type or of a.c. type, normally consist of number of smaller generators operating in parallel instead of large single unit capable of supplying the maximum load demand. These smaller units can run in single or in various parallel combinations to supply actual load for following different reasons :

Necessity of Parallel Operation of Generators

• The generating stations either of d.c. type or of a.c. type, normally consist of number of smaller generators operating in parallel instead of large single unit capable of supplying the maximum load demand. These smaller units can run in single or in various parallel combinations to supply actual load for following different reasons :

 

1. Continuity and reliability of service

The most important requirement for any generator is its continuity. This cannot be achieved if there is a single unit as in case of breakdown of prime mover or generator, there will be total unavailiability of the supply. This also affects the reliability of the supply. The requirement of uninterrupted supply is important in case of industrial loads as otherwise the economy may get affected. Thus instead of having a single large unit, number of small generators are operated in parallel.

2. Maintenance and repair

It is required to have a periodic checking and inspection of prime mover and generator to avoid the possibility of total breakdown or shunt down in future. If any of generators in under maintenance or repair then the load on that generator can be shared by other generators as all of them are working in parallel. Thus in case of failure or breakdown in any of the generators, the generator can be repaired with more care as other generators are available to maintain the service.

3. Efficiency

The load on the generating station is never constant. It varies from time to time with maximum demand occuring during morning and evening while minimum demand during late night hours. Most of the generators operate efficiently when delivering the full load. Thus when there is light load condition, it is economical to use a small, single unit. With increase in load demand, a large generator may be put in service instead of a smaller one or another smaller unit may be connected in parallel with the earlier unit which is already in service.

4. Increase in plant capacity

 Additional generators are always installed in existing plant to supply increasing load demands. Provision for the future expansion is made from the begining itself. If number of generators are operating in parallel then it is easier to add other generators for parallel operation with increase in load demand.

 

1. Parallel Operation of D.C. Generators

•In case of d.c. gnenrating stations, there are heavy thick copper bars which act as positive ans negative terminals for the entire stations. These bars are called bus bars. While connecting the d.c. generators in parallel, the positive and negative terminals of the generators should be respectively connected to the positive and negative terminals of bus bars. If the generator is connected with reverse polarity to the bars, it results in short circuit which will cause damage to the commutators and brushes, ultimately shutting down the station. Before making the parallel operation, it should be checked for reversed polarity for the generators otherwise breakers are tripped off as a result of heavy fault current.

• Consider the bus bar with positive and negative terminals as shown in the Fig. 3.30.1. The generators are connected to these bus bars for parallel operation.


• The generator 1 is connected to the bus bars and supplying to the load. Now generator 2 is to be connected in parallel.

• The prime mover of the generator 2 is started and its speed is adjusted to the rated value. Then the switch S4 is closed. The voltmeter connected across the open switch S2 completes the circuit. Now the excitation of the generator 2 is adjusted with the help of field rheostat till the voltmeter reads zero. The zero on the voltmeter ensures that the voltage of incoming generator 2 is same as that of generator 1 or the bus bar voltage. The switch S2 is then closed which connects the incoming generator 2 in parallel with the system.

• Under these conditions, the generator 2 will not take any load as its induced emf is same as bus bar voltage and there will not be any flow of current between two points at same potential. This generator is thus said to be floating on bus bars.

• In order that the generator 2 should supply current, it is necessary that its induced emf should be more than the bus bar voltage. If E is induced emf and V is bus bar voltage then the current current supplied I is given by,

I = E-V / Ra

where Ra is resistance of armature winding

• To increase the induced e.m.f. of incoming generator 2 its field is strengthened till it takes proper share of load. At the same time the field of generator 1 is weakened to maintain the bus bar voltage constant.

• In short the following procedure should be adopted while paralleling the d.c. generators :

1. The generator which is to be connected in parallel is called incoming generator. Start the prime mover of incoming generator and adjust it's speed to rated value.

2. Close the disconnected switch of the incoming generator.

3. The excitation of the incoming generator is then adjusted till it is few volts more than bus bar voltage.

4. Close the breaker of the incoming generator.

5. The shunt field rheostat of the incoming generator is adjusted to increase its voltage while the field rheostats of already connected generators are adjusted to lower their voltages till the desired load distribution which is indicated by ammeters is achieved.

a. Conditions for Parallel Operation of D.C. Generators

• The necessary conditions for satisfactory parallel operation of d.c. generators are,

1. The polarities of the d.c. generators to be connected in parallel must be same.

2. The variations in the voltage due to changes in the load should be of identical characteristics.

3. The voltages must be nearly identical so that each machine will contribute to the load sharing.

4. The prime movers driving the generators to be connected in parallel must have similar and stable rotational speed characteristics.


2. D.C. Shunt Generators in Parallel

• For stable parallel operation, the most suitable type of d.c. generator is shunt generator as it has slightly drooping characteristics. If there is any tendency for a generator to supply more or less than its proper share of load then it changes system voltage which certainly opposes this tendency. This restores the original division of load. Thus the shunt generators automatically remains in parallel, once they are paralled.

• The Fig. 3.30.1 shows the two d.c. shunt generators connected in parallel.

• If any of the generators is taken out of service then firstly its field is weakened while the field of other generators is strengthened till the ammeter associated with that generator reads zero. After this, the breaker and the concerned switch are opened to take the generator out of service. This procedure of connecting and disconnecting a generator from service prevents any shock and sudden disturbances to the prime mover or the system itself.

• If field of any generator is weakened beyond certain extent then power will be delivered to it. It will then run as a motor in its original direction. The prime mover associated with it will be thus driven due to the motoring action of the generator.

• Consider voltage-current characteristics of a shunt generator as shown in the Fig. 3.30.2 (a) and Fig. 3.30.2 (b).


• Two shunt generators are considered. For common terminal voltage, the two generators are supplying a current of I1 and 12 respectively. It can be seen that generator 2 has more dropping characteristics and supplies less current.

• The load will be divided properly within the two generators at all the points provided their voltage characteristics are similar with each generator having same voltage drop from no load to full load.

a. Load Sharing

• If the two generators are having different kW ratings then they will share a load in proportion to their ratings with their external characteristics plotted with reference to percentage of full load current as shown in the Fig. 3.30.3.


• If we consider two generators with their ratings as say 50 kW and 100 kW running in parallel and supplying a total load of 120 kW then generator 1 will supply a total load of 40 kW while the other one will supply 80 kW.

• The combined characteristics of the generators can be obtained from the individual characteristics of the generators by adding the currents provided by each generator separately at equal voltage points. From this resultant characteristics the voltage or the currents provided by the generators can be obtained. If the generators are having straight line characteristics then these results can be obtained by doing the simple calculations instead of plotting graphs.

• If the two generators having unequal no-load voltages are sharing a load then its analysis is as given below

Let E1 = No load voltage of generator 1


• The bus bar voltage can be kept constant and the load can be transferred from generator 1 to 2 by increasing either ϕ2  or N2 or by reducing N1 and ϕ1 change in N1 and N2 can be achieved by changing the speeds of prime movers while by changing the shunt field rheostats the fluxes ϕ1 and ϕ2 can be varied.

• In summary it should be kept in mind that two shunt generators in parallel having no load voltages equal will share the load in such a ratio that the load current of each machine produces the same drop in each generator. If the generators are having unequal no-load voltages and operated in parallel then the load currents should produce sufficient voltage drops in each generator so as to keep the terminal voltage same. The generator having lower voltage drop takes more share of change in load. If the generators are working in parallel and having different power ratings but same voltage regulation will divide the load in proportion to their power ratings.

 

3. D.C. Series Generators in Parallel

• Consider two d.c. series generators in parallel as shown in the Fig. 3.30.4.


• If no load voltages E1 and E2 of the two generators are initially same, generators supply equal currents aand have equal resistance for its field winding. If E1 > E2 then I1 > I2 which causes the field of generator 1 strengthened while that of 2 is weakend which will decrease E2 further. A stage is reached where generator 1 will take entire load and will also supply power to generator 2 which will start running as a motor. The two machines will form a short circuited loop which will increase the current indefinitely. This can be avoided by use of equalizer bar through which equal currents are passed in the two similar generators to the load. The slight difference in the currents therefore being confined to the loop made by the armatures and the equalizer bar.

 

4. D.C. Compound Generators in Parallel

• Consider two compound generators 1 and 2 running in parallel as shown in the Fig. 3.30.5.


• As the voltage characteristics for the usual compound generators are rising, their parallel operation is unstable in the absence of corrective devices.

• Let us consider that each generator is taking proper share of load. If for some reason, the generator 1 takes increased load slightly then the current passing through it's series field winding increases strengthening it's field to increase the generated emf. This causes generator 1 to take still more load. If system load is assumed to be constant then the load on generator 2 will decrease weakening its series field due to less current passing through its field winding which results in further decrease in its load. This effect is cumulative which leads generator 1 to take the entire load and generator 2 will be driven as motor. The circuit breakers of at least one of the two generators will open to stop the parallel operation. The under compound generators show stable operation like shunt generators.

• For stable parallel operation of over and level compound generators, equalizer bus bars are used. It is connected to the armature ends of the series coils of the generators. The equalizer bus bar is also a conductor which is not required is case of under compound generators as their characteristics are not rising.

• Now consider that the same two compound generators are operating in parallel with equalizer bar between them. If for any reason, generator 1 starts taking more load than it's proper share then it's series field current is increased. But now this increased field current will partly pass through series field winding of generator 1 and partly through series field winding of generator 2 via equalizer bar. Thus the two generators are affected in similar way preventing generator 1 from taking extra load. To have proper division of load from no load to full load is required that the regulation of each generator must be same. The series field resistances should be inversely proportional to the generator ratings.

 

Ex. 3.30.1 Two shunt generators each with a no load voltage of 200 V are run in parallel. Their external characteristics can be taken as straight lines over this operating ranges. Generator No. 1 is rated at 200 kW and its full load voltage is 190 V. Generator No. 2 is rated at 100 kW at 185 V. Calculate the bus bar voltage when the total load is 3000 A. How is the load divided between the two ?

Sol. :


 

Ex. 3.30.2 A d.c. shunt generator is supplying load connected to a bus bar voltage of 220 V. It has an armature resistance of 0.025Ω and field resistance of 110 9. Calculate the value of load current and load power when it generates an e.m.f. of 230 V. Neglect the effect of armature reaction. Draw circuit diagram.

Sol. :

The generator connected to the busbar is shown in the Fig. 3.30.6.


The busbar voltage is the terminal voltage Vt = 220 V and the load is connected to the busbar carrying current IL supplied by the generator.

At it is a shunt generator,



Ex. 3.30.3 Two d.c. compound generators are operating in parallel with an equalizer-bar coonection. Both machines are supplying a load of 1000 A. The machines have armature resistances of 0.06 Ω and 0.04 Ω, series-field resistances of 0.07Ω and 0.05 Ω and induced emfs of 420 V and 440 V respectively. Calculate: a) Current in each armature b) Current in each series-field winding  c) Current in the equalizing-bar. d) Bus-bar voltage

Sol. The arrangement is shown in the Fig. 3.30.7.



b) The total current 0f 1000 A divide




Ex. 3.30.4 Two shunt wound d.c. generators connected in parallel to supply a load of 5000 A. Each machine has an armature resistance of 0.03 Ω and field resistance of 60 Ω but the emf of one machine is 600 V and that of other is 640 V. What power does each machine supply?

Sol.:

Let


Review Questions

1. What are the reasons for the parallel operation of d.c. generators?

2. What are the conditions necessary for parallel operation of d.c. generators?

3. Explain the conditions under which two shunt generators operating in parallel share the total load in exact proportion to the machine ratings.

4. Why shunt generators are more suitable for parallel operation.

5. Two 200 V d.c. generators each having linear external characteristics, operate in parallel. One load and 220 V at a load current of 40 A, while the other has a voltage of 270 V on no load and 220 V at 50 A. Calculate the output current of each machine and the bus bar voltage when the total load is 70 A. What is the kW output of each machine under this conditions ? 

[Ans.: 230 volts, 6.9 kW, 9.2 kW] 

6. Explain the parallel operation of d.c. series generators.

7. Explain the parallel operation of two compound generators. Clearly explain why an equalizer connection is required.

 

Electrical Machines: Unit II: D.C. Generators : Tag: : DC Generators - Necessity of Parallel Operation of Generators