When the current flows through the transmission line conductors, due to its resistance there is loss which generates heat increasing the temperature.
Power Transfer Capability
of Transmission Lines
AU : Dec.-13
The main constraints in the capability
of power transfer for transmission line are thermal limit, voltage drop limit
and the stability limit. When the current flows through the transmission line
conductors, due to its resistance there is loss which generates heat increasing
the temperature. This gives the thermal limit. Thus it is required to keep the
temperature of overhead line conductors within a safe limit. This avoids
excessive line sag between the towers. It also helps in preventing irreversible
stretching maintaining the proper ground clearace. Due to this there is limit
on maximum safe current carried by overhead line.
In addition to current carried by line
conductors, the other factors such as geometry and size of conductors, spacing
between towers influence the temperature rise. The ambient temperature, wind
velocity are some of the influencing operating factors.
The underground cables are more
sensitive towards the thermal limit as there is limited possibility for heat
transfer. But there is no question of sag in case of cables. If the cables are
overheated then the insulation will start deteriorating and may get completely
damaged in the near future.
The stability limit is another
consideration in the power transfer capability of transmission lines. We have
already seen the equation for power at receiving end given by,
PR = | VS | . | VR
| / XL sin δ
For short transmission lines, the limit
for transmission capability as per above equation is given by δ = 90°. But
normally 8 is limited to 30 to 60° for maintaining the synchronism in the line.
In case of short transmission lines, the
power transfer capability is set by the thermal limit instead by stability
limit. But it is exactly opposite in case of long lines. This can be seen from
Fig. 2.20.1.
For a long transmission line
Equating the above equation with VS
= VR + B IR
With the increase in line length, β l
increases and PR decreases.
The voltage drop in the line is the main
consideration in case of medium transmission lines for maximum power transfer.
There is always rating for line in terms
of current beyond which a line is not be operated for longer duration. The
transmission lines are always designed for particular voltage level depending
on string insulators and clearances. Sometimes the rating of line is given in
terms of power which is multiplication of current and voltage. For extra high
voltage lines (EHVAC), the MVA rating is almost equal to its MW rating.
Review Question
1. Write a short note on loadability limits based on thermal
loading.
Transmission and Distribution: Unit II: (a) Modelling and Performance of Transmission Lines : Tag: : Modelling and Performance of Transmission Lines - Power Transfer Capability of Transmission Lines
Transmission and Distribution
EE3401 TD 4th Semester EEE Dept | 2021 Regulation | 4th Semester EEE Dept 2021 Regulation