Review Questions : 1. State equation for long transmission line of VS and IS in term of Vr and Ir and line parameter per unit length. Derive this hyperbolic equation and discuss i) Characteristics constant ii) Propagation constant 2. Derive expressions for the generalised A, B, C, D constants of a long transmission line by rigorous method cf analysis. 3. A3 phase transmission line 200 km long has the following constants Resistance/phase/km = 0.16 Ω, Reactance/phase/km = 0.25 Ω Shunt admittance/phase/km = 1.5 × 10-6 mho Calculate by rigorous method the sending end voltage and current when line is delivering load of 20 MW at 0.8 p.f. lagging. The receiving end voltage is kept at 110 kV. 4. Perform the analysis of long transmission lines using RIGOROUS method. 5. Explain the procedure for determining the transmission efficiency and voltage regulation of a long transmission line. AU May-05, Dec.-05, Marks 8 current relations in terms of receiving end 6. Derive for a long line the sending end voltage and voltage and current and the parameters of the line.
Rigorous Method of
Analysis of Long Transmission Line
AU : May-05, 09, 18, Dec.-05, 06, 12, 13
The Fig. 2.11.1 shows one of the phase
out of 3 phases of a long transmission line. The impedance and the shunt
admittance of the line are uniformly distributed along the length.
Let us consider a small element of the
line. Let the length of the line be dx situated at a distance of x from the
receiving end. The voltages at the two ends of the element are given as V + dV
at the sending end and V at the receiving end.
Let z
= Series impedance of the line per unit length
y = Shunt admittance of the line per
unit length
V = Voltage at the end of element
towards receiving end
V + dV = Voltage at the end of element
towards sending end
I = Current leaving the element dx
I + dI = Current entering the element dx
For small element dx,
z dx = Series impedance
y dx - Shunt admittance
The rise in voltage over the element
length in the direction of increasing x is dV which is given by,
dV = I • z dx i.e. dV / dx = I • z ... (2.11.1)
The current entering the element is I +
di whereas the current leaving the element is I. The difference in the current
di flows through the shunt admittance of the line.
Differentiating equation (2.11.1) with
respect to x,
Similarly we have after differentiating
equation (2.11.2) with respect to x
From equation (2.11.4) and (2.11.7) we
get expression for V and I in the form of arbitrary constants k1 and
k2. For finding the values of k1and k2, using
the conditions which are given as,
At x = 0, V = VR, I = IR
k1 + k2 = VR ... (2.11.8)
√ y/z [k1 - k2 ] =
IR ... (2.11.9)
Two important constants of a
transmission line which are complex quantities are as follows
Now from the equations (2.11.8) and
(2.11.9)
The sending end voltage VS
and current IS are obtained by putting x = l in the expressions
for V and I.
It is already been stated that ZC
and ɤ are complex quantities. The propagation constant ɤ can be expressed as,
ɤ = α + jβ
The real part of the propagation
constant y is called the attenuation constant a and is measured in nepers per
unit length. The imaginary part 3 is called the phase constant and is measured
in radians per unit length.
By rigorous method the solution for
sending end voltage obtained in case of long transmission line is given by,
Comparing the above equations with the
standard equations
2. Evaluation of ABCD
Constants
1) Convergent
series method (Real angle method) : As ABCD constants are the hyperbolic
functions of ɤl where ɤl = √ ZY is a complex quantity, ɤ may be
written as complex quantity equal to α + j β where α and β are both real.
cosh ɤl = cosh (α + j β) l
= cosh α l cosh j β l + sinh α l sinh j β l
= cosh α l cos j β l + jsinh α l sinh β l
Similarly, sinh ɤl = sinh (α + j
β) l = sinh α l cosh j β l + cosh α l sinh j β l
= sinh α l cos β l + jcosh
α l sin α l
Using standard tables, sinh, cosh, sin
and cos values can be obtained.
2) Convergent series method (Complex
angle method) : To evaluate hyperbolic terms in the
expression, we can make use of power series given by,
In this method, the series converges
rapidly and sufficient accuracy can be obtained by considering first few terms.
This method is preferred as compared to the method stated in (2.11.1) as it
avoids use of tables and is comparatively less laborious.
The hyperbolic functions can also be
evaluated by expressing them in terms of exponential such as
3. Evaluation of Voltage
Regulation and Transmission Efficiency
By rigorous method of analysis of long
transmission line, we have obtained the solution for sending end voltage and
current as,
Comparing above equations with standard
equations
where Y = Total shunt admittance = y l,
Z = Total series impedance = z l
Voltage regulation is nothing but change
in voltage at receiving end from no load to full load.
Thus following steps can be followed to
obtain % voltage regulation.
1. Obtain A, B, C, D parameters for the
long transmission line using given information.
where cos ϕ R is p.f. at
receiving end.
3. Obtain the magnitude of no load
voltage VRo at receiving end using the relation
| VRo | = | VS |
/ | A |
4. % Regulation of the line is then
given as,
% Voltage regulation = VRo – VR / VR
× 100
This procedure can in general be adopted
to find the regulation of any type of transmission line.
To find the transmission efficiency,
obtain the sending end current by using IS . Then find the p.f. at
sending end i.e. cos ϕ S.
Power at sending end is then given as,
PS = √ 3 VS IS
cos ϕ S
% Transmission efficiency = Receiving end power / Sending end power × 100
= PR / PS × 100
The steps for computing % transmission
efficiency can be summarized as
1. Obtain A, B, C and D parameters for
the transmission line using given information.
2. Obtain sending end voltage and
sending end current magnitudes by using following equations.
4. Compute the power at sending end
Sending end power, PS = √ 3 VS
IS cos ϕ S
5. Power at receiving end PR
may be given. Thus % transmission efficiency is then given as,
Transmission efficiency (%) = PR
/ PS × 100
Example 2.11.1
A 3 phase transmission line 100 km long has the following constants.
Resistance / phase / km = 0.15 Ω ,
Reactance / phase / km = 0.20 Ω
Shunt admittance / phase / km = 1.5 × 10-6
mho
Calculate by rigorous method the sending
end voltage and current when the line is delivering a load of 30 MW at 0.8 p.f.
lagging. The receiving end voltage is kept constant at 110 kV.
Solution : Total
resistance / phase, R = 0.15 × 100 - 15 Ω
Total reactance / phase, XL =
0.20 × 100 = 20 Ω
Example 2.11.2
Determine ABCD constants for a 3 phase 50 Hz transmission line 250 km long
having the following distributed parameters
l = 2.1 × 10-3 H/km , c = 0.014
× 10-6 F/km, r = 0.30 Ω/km
Solution :
We have,
Example 2.11.3
A three-phase overhead long transmission line has total series impedance per
phase (200 ∠
80°) Ω and total shunt admittance of (0.0013 ∠ 90°) (mho/ph).
The line deliver a load of 80 MW at 0.8 pf. lagging and 220 kV between lines.
Determine A, B, C and D parameters.
Solution :
We have,
Review Questions
1. State equation for long transmission line of VS and IS
in term of Vr and Ir and line parameter per unit length. Derive this hyperbolic
equation and discuss
i) Characteristics constant ii) Propagation constant
2. Derive expressions for the generalised A, B, C, D
constants of a long transmission line by rigorous method cf analysis.
3. A3 phase transmission line 200 km long has the following
constants Resistance/phase/km = 0.16 Ω, Reactance/phase/km = 0.25 Ω Shunt
admittance/phase/km = 1.5 × 10-6 mho
Calculate by rigorous method the sending end voltage and
current when line is delivering load of 20 MW at 0.8 p.f. lagging. The
receiving end voltage is kept at 110 kV.
[Ans : 116.67 kV, 131.1 A]
4. Determine ABCD constants for a 3 phase 50 Hz
transmission line 200 km long having the following distributed parameters
5. Perform the analysis of long transmission lines using RIGOROUS method.
AU: Dec.-12, Marks 12
6. Explain the procedure for determining the transmission
efficiency and voltage regulation of a long transmission line. AU May-05,
Dec.-05, Marks 8 current relations in terms of receiving end
7. Derive for a long line the sending end voltage and
voltage and current and the parameters of the line.
AU: Dec.-06, May-18, Marks 16
Transmission and Distribution: Unit II: (a) Modelling and Performance of Transmission Lines : Tag: : - Rigorous Method of Analysis of Long Transmission Line
Transmission and Distribution
EE3401 TD 4th Semester EEE Dept | 2021 Regulation | 4th Semester EEE Dept 2021 Regulation