With the help of circle diagram at sending end we can get PS,QS and power factor on complex plane.
Sending End Power Circle Diagram
With the help of circle diagram at
sending end we can get PS,QS and power factor on complex
plane.
The complex power at sending end is
given by,
The sending end power circle diagram is
shown in Fig. 2.17.1.
By the same method as for the receiving
end circle diagram if VR and VS are kept constant then it
can be proved that the point G' moves over a circle with centre O'. The
co-ordinates of the centre are given as,
The radius of the sending end circle is
given as,
Radius = | VS | | VR
| / | B |
The radius is same as that obtained in
case of receiving end circle diagram.
When sending end voltage is fixed, the
position of centre O' is fixed and concentric circles are obtained with radii corresponding
to different values of V R. However if |VR | is fixed and it is
required to draw sending end power circles for various values of |VS| then centre O' of sending end
circle changes and lies along O'H'. This distance O'H' varies as | VS|2
and radii of the circles will also change as |VS| keeps on changing.
If voltages |VS | and |VR
| are fixed then PS will be maximum when δ =180 – β
The sending end power circle diagram for
a short transmission line is as shown in Fig. 2.17.2.
It is obtained by using the ABCD
parameters for short line which are as follows.
Example 2.17.1
A 3 phase transmission line, 150 km long transmits a load of 80 MW at 0.8
p.f. lagging. The line voltage at the receiving end is 220 kV. The constants of
the line A - D - 0.9785 ∠
0.3°, B - 85.2 ∠
77.47 °, C - 0.000503 ∠
90.1 °
Draw receiving end and sending end
circle diagrams for the transmission line and calculate
a) Sending end voltage, current, power
factor, regulation and efficiency of the transmission line.
b) Load in kW at 0.8 p.f. lagging that
could be carried at 8 % regulation.
c) Voltage drop if the load is 120 MW at
the same power factor and the MVAR leading required for 120 MW load at 8 %
regulation.
d) Rating and power factor of
synchronous phase modifier connected in parallel with the load so that voltage
transmitted at the sending end is same as that at the receiving end.
e) Maximum power that can be transmitted
in case (d) Calculate the corresponding p.f.
Solution :
The given values are
Let scales be selected as,
1 cm - 20 MW on horizontal axis
1 cm = 20 MVAR on vertical axis
So that we have 1 cm = 20 MVA
Steps for drawing the circle diagram
1. Locate the centre O with the
co-ordinates as given above
2. Draw load line at an angle θ R = cos-1
0.8 = 36.8° to the horizontal and cut
3. From the graph OP = 10.7 cm = 214 MVA
Steps for drawing sending end power
circle diagram
1. Mark point O with co-ordinates
obtained as above
2. Draw circle with
3. Draw OO1 at angle of (β + δ)
The required answers are as follows :
a) i) Sending end voltage = 248.62 kV
(line value)
ii) Sending end current (IS)
From the sending end circle diagram
Draw the new circle with the same centre
but with radius of 10.2 cm. This circle cuts the load line at Px. Horizontal
component of O-|P-| = 0.8 cm = 0.8x20 = 16 MW which is the load carried by the
line per phase.
Total load carried at 8 % regulation = 3
× 16 = 48 MW
c) Power per phase = 120 / 3 = 40 MW
The new point P2 can be marked on the load line corresponding to this load of 40 MW.
Drop per phase = 153-127 = 26 kV
The regulation required is 8% i.e. VS
= 1.08 VR
For increased load, point P2
must move vertically downward to cut circle (2) at M2
Leading MVAR = P2M2
= 1.3 cm = 26 per phase
Total MVAR required = 26 × 3 = 78 MVAR
d) Here
Draw circle 3 with same centre but with
radius 9.45 cm. P is the operating point if no leading MVAR is supplied by SPM.
In this case the operating point M vertically downward on circle 3.
Leading MVAR = PM = 1.4 × 20 = 28 per
phase
Total MVAR = 28 × 3 = 84 MVAR
e) Maximum power under these conditions
can be found by drawing a horizontal line through O and cutting the circle at
T'
Maximum power = TT' = 7.4 cm = 148 MW
per phase = 444 MW for 3 phase
Power factor angle corresponding to this
condition is 50.1°
p.f. = cos θ = cos 50.1° = 0.641
leading
Example 2.17.2 The constants of a three phase line are A = 0.9Z2° and B = 140Z 70° ohms per phase. The line delivers 60 MVA at 132 kV and 0.8 pf lagging. Draw power circle diagrams and find (a) sending end voltage and power angle (b) the maximum power which the line can deliver with the above values of sending and receiving end voltage (c) the sending end power and power factor (d) line losses.
Solution : The
given values are
Steps for drawing the sending end circle
diagra, are as given below.
1) Locate the centre O with the co-ordinates as given above
2) Draw load line at an angle ϕR
= cos10.8 = 36.86° to the horizontal and cut
3) From the graph OP = 13.9 cm = 55.6
MVA
The receiving end circle diagram is
shown in the Fig. 2.17.4 (a)
2) Sending end circle diagram
Steps for drawing the sending end circle
diagra, are as given below.
1) Mark point O with co-ordinates given
as above
2) Draw circle with radius
3) Draw OO1 at an angle of (β
+ δ) = 82°
Sending end voltage (line value) =
176.89 kV
O1P = 4.8 cm = 19.2 MVA (from
circle diagram)
The sending end circle diagram is shown
in the Fig. 2.17.4 (b)
Line Losses - Sending end power -
Receiving end power = 53.02 - 48 = 5.02 MW
Maximum power that can be transferred
PRmax = N1 P1
= 10.4 cm = 10.4 × 4 = 41.6 MW per phase
For 3 phase max power transferred = 3 PRmax
= 3 × 41.6 = 124.8 MW
Review Questions
1. Explain how sending end power circle diagram can be drawn.
2. A 275 kV three phase line has the following parameters
A = 0.93 ∠1.5°, B = 115 ∠77°
If the receiving end voltage is 275 kV calculate using circle
diagram.
a) The sending end voltage required if a load of 250 MW at 0.85
lagging pf. is being delivered at the receiving end.
b) The maximum power that can be delivered if the sending end
voltage is held at 295 kV.
c) The additional MVA that has to be provided at the receiving end
when delivering 400 MVA at 0.8 lagging pf. the supply voltage being maintained
at 295 kV.
[Ans.: 355.5 kV, 556 MW, 295 MVA]
3. A symmetrical 132 kV line delivers a load of 40 MW at 0.8
lagging of calculate with the help of circle diagram
a) The sending end voltage
b) The MVAR capacity of the synchronous condenser needed if the
sending end voltage is increased to 180 kV.
c) The capacity of synchronous condenser needed at no load if the
receiving end and sending end voltages are 132 kV respectively. Assume line
constants are A = 0.9 ∠25°,
B = 100 ∠ 70°Ω, C = 0.0006 ∠ 88°.
[Ans.: 227.4 kV, 84 MVAR, 84 MVAR]
4. A 3 phase overhead line has per phase resistance and reactance
of 6 Ω and 20 Ω respectively. The sending end voltage is 66 kV while the
receiving end voltage is maintained at 66 kV by a synchronous phase modifier.
Determine the kVAR of the modifier when the load at the receiving end is 75 MW
at 0.8 pf. lagging also determine the maximum load that can be transmitted.
[Ans.: 96.95 MVAR, 148.67 MW]
Transmission and Distribution: Unit II: (a) Modelling and Performance of Transmission Lines : Tag: : Steps for drawing - - Sending End Power Circle Diagram
Transmission and Distribution
EE3401 TD 4th Semester EEE Dept | 2021 Regulation | 4th Semester EEE Dept 2021 Regulation