The nonuniformity in the voltage distribution over a string of suspension insulators is expressed in terms of a parameter called "string efficiency".
String Efficiency
AU : Oct.-01, April-98, 99, 05, May-04,
07, 11, 12,15,18, Dec.-05, 08, 11, 13,16
The nonuniformity in the voltage
distribution over a string of suspension insulators is expressed in terms of a
parameter called "string efficiency".
The string efficiency is defined as the
ratio of total voltage across the string to the product of number of units and
the voltage across the unit adjacent to the line conductor.
Mathematically it can be expressed as,
where n = Number of units or discs in the string
The string efficiency is calculated
based on the string used for each line and hence the voltage across the string
is the voltage of conductor with respect to earth i.e. phase voltage.
More the value of the string efficiency,
more uniform is the voltage distribution across the string. For the ideal case,
the string efficiency is 100 % and the voltage across each disc of the string
is equal. Practically various methods are used to obtain the string efficiency
as high as possible.
In the rainy season, insulators are wet
and the mutual capacitance value increases. Thus the ratio of shunt to mutual
capacitance i.e. k decreases. This increases the uniformity of the voltage
distribution. Hence in rainy season, string efficiency is higher.
Consider a string of suspension
insulator consisting of 4 discs. The voltage distribution will be as shown in
the Fig. 5.5.1.
Let C1 = kC
Thus the shunt capacitance is k times
the mutual capacitance.
Applying Kirchhoff's current law at node
P,
I2 = i1 + I1
... (5.5.1)
The current through capacitor is the
ratio of voltage across capacitor and the capacitive reactance of the
capacitor.
Similarly applying Kirchhoff's current
law at node Q,
I3 = i2 + I2 ... (5.5.3)
Note that the voltage across the shunt
capacitance C1 carrying current i2 is V1 + V2.
Note that the voltage across the shunt
capacitance C1 carrying current i3 is (V1 + V2
+ V3)
Hence using equations (5.5.2), (5.5.4),
(5.5.6) and (5.5.7) all the voltages for given value of k can be calculated.
Thus it can be seen that the voltage
across the unit nearest to the line conductor is maximum.
Now String efficiency = V / n × V4
= 6.8906 V1/ 4 × 2.8281 V1 for n 4 60.91 %
Thus for n = 4 and k = 0.25, the string
efficiency is just 60.91 %. More the value of k, greater is the nonuniformity
and lesser is the string efficiency. While as the number of units in a string
increases, the string efficiency decreases and its calculation becomes much
more tedious. Hence the string with less number of units is more effective.
Example 5.5.1
Each line of a three phase system is suspended by a string of three similar
insulators. If the voltage across the line unit is 20 kV, calculate the line to
neutral voltage and the string efficiency. Assume that the shunt capacitance
between each insulator and earthed metal work of tower to be 1/10th of the
capacitance of the insulator.
Solution:
The arrangement is shown in the Fig. 5.5.2.
Applying Kirchhoff's current law at node
P,
Now V3 is voltage across line unit which is closest to the line conductor, given as 20 kV.
It can be noted that if the capacitance between insulator and line conductor is neglected then the equations for the voltage distribution across the insulators of a string remain same as derived and can be used directly to solve the problems.
Example 5.5.2
An insulator string consists of three units, each having a safe working
voltage of 15 kV. The ratio of self to shunt capacitance is 6:1. Find the
maximum safe working voltage of the string and the string efficiency.
AU : April-99, Oct.-Ol, April-05,
May-11, 12, Dec.-17, Marks 16
Solution :
Let C1 = shunt capacitance and C = Self capacitance
C / C1 = 6 / 1
C1 = 1/6 C i.e. k = 1/6
= 0.1667
Let voltage across line unit be 15 kV
which is its safe working voltage i.e.V3 = 15 × 103 V.
This is because the maximum voltage appears across the line unit.
For insulator string of 3 units we get,
Example 5.5.3
An insulator string for 66 kV line has 4 discs. The shunt capacitance
between each joint and metal work is 10 % of the capacitance of each disc. Find
the voltage across the different discs and string efficiency.
Solution :
Let = Shunt capacitance and C = Self capacitance
The arrangement of disc is shown in the
Fig. 5.5.4.
Example 5.5.4
In a 33 kV overhead line, there are three units in the string of insulators.
If the capacitance between each insulator pin and earth is 11 % of self
capacitance of each insulator, find the distribution of voltage over 3
insulators and string efficiency. Draw the equivalent circuit.
Solution :
Let, C1 = Shunt capacitance
C = Self capacitance
Applying KCL at various nodes P, Q and
R.
Example 5.5.5 In
a 3 unit insulator, the joint to tower capacitance is 20 % of the capacitance
of each unit. By how much should the capacitance of the lowest unit be
increased to get a string efficiency of 90 % ? The remaining two units are left
unchanged.
AU : May-15, Marks 16
Solution :
The arrangement is shown in the Fig. 5.5.6.
C1 = 0.2 C, k = 0.2
Applying KCL at node P,
Thus the initial capacitance of last
unit C is to be increased to 1.267 C to get string efficiency of 90 %. Hence
increase in the capacitance of the third unit is 0.267 i.e 26.7 %.
Example 5.5.6
A string of 6 insulator units has self capacitance equal to 10 times the pin
to earth capacitance. Find
a) Voltage distribution from top to
bottom insulator as a percentage of the total voltage.
b) The string efficiency.
Solution :
The arrangement is shown in the Fig. 5.5.7.
Let C1 = Shunt capacitance
and
C = Self capacitance
C = 10 C1
C1 = kC = 0.1 C
k = 0.1
Applying KCL at various nodes,
Example 5.5.7
In a 5 insulator disc string, capacitance of each unit and earth is 1th / 6 of
the mutual capacitance. Find the voltage distribution across each insulator in
the string, as a percentage of voltage of conductor to earth. Find also the
string efficiency.
Solution :
The string is shown in the Fig. 5.5.8.
C1 = kC = 1/6 C
Applying KCL at various nodes P, Q, R
and S and using,
Example 5.5.8
A 3 phase overhead transmission line is being supported by three disc
insulators. The potentials across top unit and middle unit are 9 kV and 11 kV
respectively. Calculate (i) the ratio of capacitance between pin and earth to
the self-capacitance of each unit (ii) the line voltage and (iii) string
efficiency.
AU : Dec.-11,Marks 16
Solution :
The arrangement is shown in Fig. 5.5.9.
Review Questions
1. Define string efficiency.
2. Derive the expression for the string efficiency of a 3 disc
string.
3. Explain the procedure cf calculating the string efficiency of a
4 unit string.
4. Considering a suspension insulator string of 4 units, obtain
expressions for the voltages across various units in terms of V1 the
voltage across the top most unit and m is the ratio between ground capacitance
and mutual capacitance.
[Ans.: V2 = V1 (l + m), V3 =
V1 (m2 +3m +l), V4 = V1(m3
+ 5m2 + 6m +1)]
5. Each line of a 3 phase system is suspended by a string of 3
similar insulators. If the voltage across the bottom most unit (line unit) is
17.5 kV, calculate the voltage across the insulator string. Also find the
string efficiency. Assume that the earth capacitance is 1th/8 of mutual capacitance.
[Ans: 44.241 kV, 84.268 %]
6. A three phase overhead transmission line uses suspension
insulator using 3 insulator units. The voltage across the top unit is 10 kV and
that across the middle unit is 11 kV. Calculate,
i. Ratio of shunt to self capacitance ii. String efficiency iii.
Line voltage
[Ans.: 0.1,86.7 %, 59 kV]
7. Each line cf a three phase system is suspended by a string of 3
similar units. If the voltage across the line unit is 22 kV, calculate the line
to neutral voltage and string efficiency. Assume that the shunt capacitance
between each insulator and earthed metal work of tower to be l/8th of the
capacitance cf the insulator.
[Ans.: 55.6175 kV, 84.26 %]
8. Three busbar conductors in outdoor substation supplied by the
units of post insulators. Each unit consists of stack of 3 pin insulators. The
voltage across line unit is 9 kV while that across middle unit is 7.5 kV. Find
the busbar voltage of station.
[Ans.: 39.9019 kV]
Transmission and Distribution: Unit III: (b) Insulators : Tag: : Method of Calculating - String Efficiency
Transmission and Distribution
EE3401 TD 4th Semester EEE Dept | 2021 Regulation | 4th Semester EEE Dept 2021 Regulation