The insulators are tested according to the standards. The following tests are performed while testing an insulator : 1. Mechanical tests 2. Electrical insulation tests 3. Environmental tests 4. Temporary cycle tests 5. Corona and radio interference tests.
Testing of insulators
The insulators are tested according to
the standards. The following tests are performed while testing an insulator :
1. Mechanical tests
2. Electrical insulation tests 3.
Environmental tests 4. Temporary cycle tests 5. Corona and radio interference
tests.
These tests are further grouped into
three classes according to the standards which are,
1. Type tests :
These tests are performed to judge the design and specified ratings of the
insulator. These tests include mechanical tests and electrical flash over
tests.
2. Sample tests :
These are performed to judge the material used, its quality and mechanical
properties. These are also called performance tests. These include some
mechanical tests.
3. Routine tests :
On every insulator some standard tests are performed called routine tests.
The mechanical tests are performed to
judge the ability of an insulator to withstand various mechanical stresses. The
mechanical tests include :
1. Mechanical strength test 2.
Compression test 3. Torsional test
4. Minimum bending test 5. Mechanical
vibration test
In each of these tests, an insulator is
subjected to a particular mechanical stress, for particular specified time. The
insulator must be capable of sustaining the mechanical stress as per the
specifications associated with it.
These tests are performed to judge the
electrical properties of the insulation under test. The main test in this
category is the flash over test.
Flash over tests are further classified
as,
1. 50 Cycle Dry Flash-Over Test :
In this test, the voltage is applied between the electrodes of the insulator
and is gradually increased. The voltage at which the surrounding air breaks
down is called the flash-over voltage. This voltage must be greater than the
specified limit. Insulator must sustain the minimum voltage for one minute.
2. 50 Cycle Wet Test :
The test is conducted similar to the dry test but in addition to the applied
voltage, the water is sprayed over the surface at an angle of 45°, resembling
the raining condition. The insulator must be capable of withstanding the
minimum standard voltage for 30 seconds under wet conditions. The wet test is
applicable only to the outdoor insulators.
Other electrical tests include,
1. Power frequency withstand test :
Normal power frequency voltage is continuously applied to the insulator. This
causes dust particles to align on the surface causing leakage currents. The
flash-over is avoided. The voltage magnitude is twice the specified rated
voltage. It is applied for 1 minute. There should not be flash-over or
puncture. This is a type test as well as routine test.
2. Impulse voltage withstand test :
In this test, standard impulse voltage surge is applied to the insulator. Such
surges are caused due to the lightning in practice. The standard lightning
impulse wave is of 1.2 µsec wave front and 50 psec wave tail hence called
1.2/50 impulse wave. For this test, the generator developing the lightning voltage
surges is used.
The impulse voltage at very high
frequency of several hundred thousands Hz is applied to the insulator and the
spark over voltage is noted down. The impulse ratio is defined as,
Impulse ratio = Impulse spark over
voltage / 50 cycles per sec spark over voltage
This ratio should be 1.4 for pin type
while 1.3 for suspension type insulators.
3. Puncture voltage test :
In this test, the insulator is suspended in the oil and certain minimum voltage
is applied. This value in case of suspension insulator is 1.3 times the dry
flash over voltage. The insulator should not puncture under this test.
In these tests the insulator is
subjected to the alternate temperature cycles, sudden temperature changes, pollution
and some other environmental stresses. Out of these tests, for extra high
voltage insulators sudden temperature drop test, extremely low temperature test
and pollution test are compulsory tests.
In temperature cycle test, the insulator
is heated in water at 70 °C for one hour and is then immediately cooled in
water at 7 °C for another hour. Such three cycles are repeated. Then the
insulator is dried. After this test, the glaze of the insulator should not be
damaged.
When the voltage stress level increases
beyond corona inspection level, corona discharge starts. The corona discharge
means the violet glow, hissing noise and production of ozone gas around a line.
This causes inductive interferences with neighbouring communication lines. By
providing suitable voltage grading rings, smooth surface and higher size of
conductors, corona discharge and radio interference can be eliminated for
certain voltage range.
These tests include,
1. Porosity test : This
is also called destructive test. The insulator under test is broken into pieces
and immersed in a 1 % solution of dye in alcohol under a pressure of 140 kg/cm2
for about a day. Then the samples are removed and inspected. The porosity is
indicated by the deep penetration of the dye into it.
2. Proof load test :
All types of the insulators are assembled and a tensile load of 20 % in excess
of specified load is applied, for about one minute.
3. Galvanising test :
In this test, galvanised metal parts of the insulator are tested for the
strength of galvanization.
4. Corrosion test :
The insulator is tested against the corrosion. In this test, insulator is
suspended in a copper sulphate solution at 15.6 °C for one minute. Then it is
removed, dried, cleaned and again put it in the solution. The cycle is repeated
for four times and there should not be any type of deposition on the metal. Out
of these tests, proof load and corrosion are routine tests. For special type of
insulators, some more tests may be performed as per the decision of supplier
and the consumer.
Review Question
1. Explain the various tests conducted on insulators.
Transmission and Distribution: Unit III: (b) Insulators : Tag: : Mechanical - Electrical Insulation - Environment and Temporary Cycle - Corona and Radio Interference T- Other Important - Testing of insulators
Transmission and Distribution
EE3401 TD 4th Semester EEE Dept | 2021 Regulation | 4th Semester EEE Dept 2021 Regulation