Question : 1. Discuss the design of primary distribution system with respect to i) Selection of voltage ii) Choice cf scheme iii) Size cf feeders.
Design Considerations for
Primary Distribution
The design of primary distribution is
based on the following considerations,
1. Selection of voltage :
The commonly used voltage levels for primary distribution are 33 kV, 11 kV and
6.6 kV. The selection depends on the available load estimation of the area. The
highest voltage which is economically justified is selected, keeping in
consideration, the future possible load demand.
The economic comparison over the period
of time considered for the planning, decides the proper voltage level. The
number of plans based on different possible voltage levels are prepared,
considering a period of 8 to 10 years. The cost is compared by dividing the
schemes into the steps to be taken at particular years. All the schemes are
identical in capacity and reliability. The voltage level giving most economical
scheme is selected.
The economical voltage level is selected
based on an available empirical formula given by,
V = 5.5 √ 0.62 L + 3p/100
where V = Line voltage in kV, L =
Distance in km
P = Maximum power per phase to be
delivered in kW
The standard higher voltage nearest to
the value given by above formula is generally selected. The value must be
selected such that the line voltage regulation remains well within the limits.
2. Choice of scheme :
The choice of scheme is based on the various considerations such as economy,
reliability, safety from consumer point of view, efficiency, load to be
supplied and overall appearance.
For low and medium load density
locations, a radial distribution system is used. If the reliability of supply
is of great importance from the load point of view then parallel feeders are
used. For high load density areas ring main distribution scheme is used.
The number of feeders to be used depends
on the various factors such as total load to be supplied, permissible voltage
drop, the load density, the distance upto secondary distribution, proper
locations for secondary distribution etc.
3. Size of feeders :
The size of the feeder conductor is determined on the basis of,
i) Current carrying capacity.
ii) Permissible voltage drop in the
feeder.
iii) Economic consideration.
Each of these considerations may give
different sizes. Basically the feeder size is decided based on current carrying
capacity and then modified based on voltage drop and economic consideration.
The current carrying capacity depends on the conductor losses and surroundings.
The current carrying capacity is decided for a maximum working temperature of
75 °C. Standard tables are available for the current carrying capacities of
different ACSR conductors for various operating temperatures for both overhead
lines as well as underground cables. Using the table, maximum current capacity
of conductor and its tentative size is determined. The tables for conductor
resistances and inductances are also available. Hence the voltage drop in the
feeder due to rated current can be determined. If the drop is small then it can
be adjusted by selecting the turns ratio of the transformer at the secondary distribution.
But if voltage drop is high then alternative size must be selected so as to
reduce the voltage drop. The size is then compared with the size obtained from
Kelvin's law for economical aspects.
Review Question
1. Discuss the design of primary distribution system with respect
to
i) Selection of voltage ii) Choice cf scheme iii) Size cf feeders.
Transmission and Distribution: Unit V: (a) Distribution Systems : Tag: : Distribution Systems - Design Considerations for Primary Distribution
Transmission and Distribution
EE3401 TD 4th Semester EEE Dept | 2021 Regulation | 4th Semester EEE Dept 2021 Regulation