Consider a three phase line consisting of three conductors a, b and c as shown in the Fig. 1.17.1. These three conductors are equally spaced at the comers of an equilateral triangle having radius r.
Inductance of Three Phase
Lines with Equilateral and Symmetrical Spacing
Consider a three phase line consisting
of three conductors a, b and c as shown in the Fig. 1.17.1. These three
conductors are equally spaced at the comers of an equilateral triangle having
radius r.

The flux linkages of conductor a are
given by,

If the currents are assumed to be
balanced then

Because of symmetry, conductors b and c
will have same inductance as that of conductor a. Each phase consists of only
one conductor. So the above equation gives inductance per phase of the three
phase lines. For stranded conductor we write Ds whereas for single conductor it
is replaced by r'.
Example 1.17.1
A three phase transmission line 100 km long has its conductors of 1.63 cm
diameter spaced at the corners of an equilateral triangle of 100 cm side. The
arrangement is as shown in the Fig. 1.17.2. Find the inductance per phase of
the system.

Solution :
D = Distance between the conductors = 3 m

Example 1.17.2 A
three phase line with equilateral spacing of 3 m is to be rebuilt with
horizontal spacing (D13 = 2 D12 = 2 D32). The
conductors are to be fully transposed. Determine the spacing between adjacent
conductors such that the new line has the same inductance as the original
line.
Solution :
Consider the three phase line with equilateral spacing. Let us find the
inductance of this line.
D = Distance between the conductors = 3
m
Let r be the radius of each of the
conductors.


The inductance of the line per phase per
km is given by,

This line is to be rebuilt with
horizontal spacing such that

The radius of the conductor remains same
as r
The inductance per phase per km with
this arrangement is given by,

Equating equations (I) and (II) as the
inductance in both the arrangements remains same.

Review Questions
1. Derive an expression for the inductance of a three phase
overhead transmission line when conductors are symmetrically spaced.
2. Find the inductance per km of a three phase transmission line
using 1.24 cm diameter conductors when these are placed at the corners of an
equilateral triangle of each side 2 m.
[Ans.: 1.2052 × 10-3 H/km]
3. A three phase transmission line 100 km long has its conductors of 0.6 cm diameter spaced at the corners of an equilateral triangle of 100 cm side. The arrangement is as shown in the Fig. 1.17.4. Find the inductance per phase of the system.
[Ans.: 0.1211 H]