Question : 1. State the advantages of GIS.
Gas Insulated Switchgear
Substation (GIS)
Gas insulated substations make use of
sulfur hexafluoride (SF6) gas. SF6 gas has excellent dielectric properties when
used at moderate pressure for phase to phase and phase to ground insulation.
The high voltage conductors, circuit breaker interrupters, current
transformers, voltage transformers, switches and lightning arresters are
enclosed in SF6 gas inside grounded metal enclosures.
SF6 gas has higher dielectric strength
than air and the conductors and contacts are insulated by pressurized SF6 gas
indicating smaller clearenes as compared to AIS substations phase to phase
spacing is considerably reduced thus requiring lesser space as compared to AIS
substation of same capacity. In urban environment this proves to be
advantageous due to unavailability of land and their increasing prices. Thus
GIS substations are installed where the land requirement for erection of
substation is limited and expensive such as in large cities and towns. The
overall size of each equipment and complete substation is significantly reduced
to about 10 % in comparision with conventional AIS substions.
GIS substations can be a preferable
choice in large cities and towns, mountains and valley regions, underground
substations, off shore substations and power stations and in highly polluted
and saline environment.
The compartments used in SF6 gas
insulated substations and those used in conventional outdoor substations are
same. The live parts are encapsulated in metal housings which are filled with
SF6 gas. The cast resin insulators form the support for the live parts while
some of the insulators are barriers between adjacent modules so that the gas is
restricted from passing through them.
The total installation is subdivided
into verious compartments. These are gas tight with respect to each other. Each
compartment has independent gas monitoring system which is simple. The gas
density in each compartment is monitored while the pressure of the gas is
maintained at a proper value. With slight reduction in pressure, the gas is
automatically trapped up low pressure alarm is sounded with leakage of gas
resulting in automatic tripping.
The enclosures are made up of
non-magnetic materials such as stainless steel or aluminium. The enclosures are
earthed. The tightness of gas is provided by using static 'O' shaped seals
which are placed between machined flanges.
The merits of gas insulated substations
are as given below :
1. These are safe since the metal
enclosures are earthed, the operating personnel are protected. They are
reliable.
2. It takes lesser space as compared
with conventional AIS substations.
3. It has long service life with less
maintenance requirement.
4. It has lower weight due to aluminium
enclosures.
The demerits of GIS substations are as
given below :
1. It is constlier as compared to AIS
installations.
2. Supply of SF6 gas at the site and its
procurement is sometimes poses problems.
3. It requires separate building due to
indoor nature of these substations.
4. Dust or moisture inside the
compartments may cause flash overs.
5. The outage period under the event of
fault is more with severe damage.