Question : 1. Draw and explain key diagram of 11 kV/400 V substation.
Key Diagram of 11 kV / 400
V Indoor Substation
Fig. 8.8.1 shows the key diagram of 11
kV/400 V indoor substation. The explanation is as given below.
The 3 phase, 3 wire 11 kV is tapped at
the substation and connected to gang operated switch which contains isolators
in each of its phase.
From the gang operated switch, with the
help of underground cable the line is taken to the indoor substation and
connected to the High Tension (H.T.) side of the transformer through circuit
breaker. The transformer steps down the voltage from 11 kV to 400 V and
secondary uses 3 phase, 4 wire system for distribution.
The CTs are placed at suitable locations
which are used to supply metering and indicating instruments and relay
circuits.
The secondary side of the transformer is
connected to the bus bars through main circuit breaker which is normally of oil
type. The 3 phase, 4 wire supply is further given to various consumers through
circuit breakers.
Between any two lines the voltage is 400
V while the voltage between any one phase and neutral is 230 V. The three phase
supply can be used to meet three phase type of loads such as motors, furnaces
etc. while single phase supply is used for single phase loads such as
residential load containing tubes, fans and other equipments.
Review Question
1. Draw and explain key diagram of 11 kV/400 V substation.
Transmission and Distribution: Unit V: (b) Substations and Grounding : Tag: : - Key Diagram of 11 kV / 400 V Indoor Substation