Q.1 Define a substation.
Ans. : A substation is
defined as the assembly of apparatus which is used to change the characteristics
of supply system such as voltage, frequency, a.c. to d.c. or power factor.
Q.2 How will you select an ideal
location for a distribution substation ?
Ans. : Following
factors are to be taken into consideration while selecting an ideal location
for a substation.
1. Availability of suitable and
sufficient land
2. Facility for communication
3. Avoiding area causing atmospheric
pollution
4. Easy operation and maintenance
5. Adequate drainage facility
Q.3 State the functions of a circuit
breaker.
Ans. : Following are
functions of a circuit breaker,
1. Carrying full load current
continuously.
2. Opening and closing the circuit on no
load.
3. Making and breaking normal operating
current.
4. Making and breaking fault currents of
magnitudes upto which it is designed for.
Q.4 Name the factors that should be
taken care of while designing and erecting a substation.
Ans. : The design and
erection of a substation involves civil work after proper site selection and
electrical work. The electrical design of substation involves choice of bus bar
arrangement , transformer selection, selection of various protective and
measuring devices such as isolators, circuit breakers, relays and lightning
arrestors etc. The provision of facilities such as earthing, cabling, oil
handling, illumination, communication etc.
Following factors are to be taken into
consideration while erecting a substation :
1. Type of substation
2. Availability of suitable and
sufficient land
3. Facility for communication
4. Avoiding area causing atmospheric
pollution
5. Easy operation and maintenance
6. Drainage facility
Q.5 State the advantages of outdoor
substation over indoor substation.
Ans. : Following are
the advantages of outdoor substation over indoor substation :
1. Time required for erection is less
2. Future expansion is easier
3. The capital cost required is less
4. All equipments are within view and
the fault location is easier
5. The cost of switchgear installation
is less and amount of building material required is small.
Q.6 What is function of isolators ?
Ans. : The function of
isolators is to disconnect a part of power system for repair and maintenance
and operated after switching off the load by means of a circuit breaker.
Q.7 State the conditions for laying out
a substation.
Ans. : Following are
the conditions for laying out a substation :
1. The arrangement provided by a
substation must be safe and reliable.
2. The site should be properly located
with good atmospheric conditions.
3. Capital cost requirement should be
small.
4. Operation and maintenance must be
easier.
Q.8 Mention the significance of neutral
grounding.
Ans. : The earthing or
grounding is nothing but the connection of neutral point of the supply system
to the general mass of the earth in such a way that immediate discharge of
electricity can take place without danger. It ensures safety of personnel or
human beings against electrical shocks (including animals and plants) and
equipments. It also avoids accidents which otherwise may take place. The
equipment is also protected against lightning and voltage surges. The voltage
stress on the lines is also reduced along with that on the equipment with
respect to earth under abnormal conditions.
Q.9 What are objectives of earthing ?
Ans. : Following are
the objectives of earthing
i. It should provide adequate safety of
operating personnel/human being (including animals and plants) against
electrical shocks /hazards and avoid accidents.
ii. It should provide an alternative
path for the fault current to flow so as to reduce danger of the user.
iii. It should ensure that all the
exposed conductive parts do not reach a dangerously high potential and should
reduce the stress on the lines along with that on the equipment with respect to
earth under abnormal conditions.
iv. It should be able to maintain the
voltage at any part of an electrical system at a known value so as to avoid
excessive voltage on the appliances or equipment or over current situation.
Q.10 What are various methods of
earthing in substations ?
Ans. : The earthing in
substations is carried out with the help of equipments such as electrodes,
driven rods, risers and grounding grid or mat consisting of number of meshes
and connected to several earth electrodes driven at intervals. The various
methods adopted for earthing are
i. Solid or effective grounding
ii. Resistance grounding
iii. Reactance grounding
iv. Resonant grounding
Q.11 Write are advantages of neutral
grounding ?
Ans. : Following are
advantages of neutral grounding
i. The faulty part can be isolated from
the remaining system with the help of earth fault relays.
ii. The transient voltage in the system
with grounded neutral is small.
iii. The arcing grounds are prevented
from occurring by using suitable switchgears.
iv. The voltage of healthy phases during
faulty condition remains nearly constant as the neutral point is not shifted.
v. The static charges which gets induced
are grounded immediately. This avoids disturbance in the system.
vi. Reliability of the system is
improved.
vii. The discriminative type of fault
indicator can be installed on such systems.
Q.12 What is need of an earthing system
?
Ans. : In order to
provide safety of personnel or human beings against electrical shocks
(including animals and plants), to reduce the possibility of getting electrical
shocks and avoiding accidents, to protect the equipments, buildings,
machinery/appliances against lightning and voltage surges, to reduce stress on
the lines along with that on the equipment with respect to earth under abnormal
conditions earthing is required.
Q.13 State the disadvantages of
ungrounded neutral.
Ans. : Following are
the disadvantages of ungrounded neutral
i. Under faulty condition, large
transient voltages with magnitude several times that of normal value is
produced causing the breakdown of insulation resulting in damage of the
concerned equipment.
ii. System cannot be protected from
earth fault and arcing ground may occur.
iii. There is no path to earth for
voltages due to lightning surges.
Q.14 What are terminal and through substations
?
Ans. : In terminal
substation, a line which is supplying to that substation ends or terminates.
Its location is either at the end of the main line or may be at a point away
from main line route.
In through substation, the incoming line
is not terminated but it passes through at the same voltage and the tapping is
taken which feeds the transformer.
Q.15 What are the materials mainly used
in bus bars ?
Ans. : The
bus bars are either rigid type or strain type. For rigid type bus bars, copper
or aluminium bars are used. Such bus bars are used for low and medium voltage
levels. For strain type bus bars mainly stranded aluminium (ACSR) conductors
are used which are supported by strain insulators. The strain type bus bars are
used for high voltage levels.
Q.16 What are the classifications of
substation according to service ?
Ans. : According to
service, the substations are classified as :
1. Transformer substations :
In these substations, power is transformed from one voltage level to other.
These are further classified as,
transmission or primary substation, subtransmission or secondary substation and
step down or distribution substation.
2. Industrial substations :
For industries demanding huge power, a seperate substation is installed.
3. Switching substations :
These are used for switching operations of power lines.
4. Synchronous substations :
These are used for synchronous phase modifiers used for the improvement of
power factor.
5. Frequency change substations :
These are used for converting normal frequency to other useful frequency.
6. Converting substations :
These are used for converting a.c. to d.c. required for electric welding,
battery charging etc.
Q.17 What are the major equipments of a
substation ?
Ans. : Refer section 8.4.
Q.18 What is gas insulated substation 7
Ans. : Gas insulated substations make use of sulfur hexafluoride (SF6) gas. SF6 gas has excellent dielectric properties when used at moderate pressure for phase to phase and phase to ground insulation. The high voltage conductors, circuit breaker interrupters, current transformers, voltage transformers, switches and lightning arresters are enclosed in SF6 gas inside grounded metal enclosures.